Some questions for choosing an uninterruptible power supply (UPS) unit for a new workstation, questions that came up when I realized how ignorant I am about these things.
One thing I do understand is that a VA rating is not the same as the watts actually supplied. Up until now, I just assumed that 1000 VA was "plenty" and blithely went on my way. I now understand a UPS unit rated at 1000VA may actually carry only 500 to 700 watts which would not be enough for the new workstation I'm hurriedly assembling.
So, for a feeding a computer with a 910 watt Power Supply Unit (PSU), what Uninterruptible Power Supply (UPS) specs should I look for?
If my probable maximum load is 800 watts but my PSU is rated higher, should I match the UPS unit to the probable maximum load or to the PSU’s maximum rating? I found these calculator/charts for sizing a PSU, which I am thinking also may be useful for guesstimating the maximum load that a UPS might need to carry:
Power Supplies: How Much Power Do You Need? (http://www.pcpower.com/technology/power_usage/)
Power Supply Selector (http://www.pcpower.com/Power_Supply_Selector.html)
For me, it looks like I might have a maximum load of roughly 775-800 watts. I'm getting a PSU with some headroom. I suspect that ought to match the PSU and UPS, but I do not know.
How does Automatic Voltage Regulation (AVR) work? When running on line voltage (as opposed to batteries), is AVR limited in any way by the power rating for battery operation? Or does AVR basically work like a line conditioner and provide stable power to whatever is hooked up to it regardless of what the UPS unit might supply if it were on battery?
How tightly does AVR have to work to be safe with the newer generations of PSU and CPUs (such as the I7-3930k)? For instance, I have been using a Tripp-Lite G1000UB with the old system. We have dirty power here. Today, the line voltage from the tap was bouncing between 123 volts and 115 volts. (Obviously, I’m in the North America and we’re talking 60 Hz power). I put a VOM on a power-out cable from the Tripp Lite unit. The output from the UPS was hovering around 119.8, although slowly fluctuating as far down as 119.5 and up occasionally to 120.00. Checking specs for UPS units shows a lot of them listing output at “120 v +/- 5%.” That means the tolerance is 6 volts above or below 120 v, right? So, the AVR on my existing unit is working okay, right? The small variation between 119.5 v and 119.9 v is nothing to worry about, right?
Do I need “pure sine wave” output from my UPS if the PSU manufacturer does not spec it in the manual or on the web site? (PC Power & Cooling does not spec it for the 910 Watt unit I have purchased.)
Prices for UPS units rated up to 1000 watts are about half (or less) of the cost of units rated over that. If a power outage occurs while my workstation is, say, in the middle of a long session transcoding 1080 AVCHD to Blu-ray or DVD, I’m guessing that there will not be a full load. A big load, but not the max. The processor will be high but only some of the disks and the raid card will be pulling power. Is this a reasonable assumption or not? Or, with a 900 watt power supply, should I be looking at a UPS unit that carries, say, 1500 watts?
Also, given that price differential, should I plan on using a sub-1000 watt UPS unit exclusively for the workstation and not plug anything else into it? (For example, since I work with twin monitors, should I keep the present Tripp-Lite unit for feeding power to the monitors?)
I’ve assembled a preliminary list of possible candidates for purchase. Depending on what is said in reply to my questions, some of these will drop off the list. But for now, I will be grateful for comments from anybody who has experience with any of these units or who feels knowledgeable enough to help make a selection.
Tripp Lite SMART1500LCD Smart Pro Digital 1500 VA 900 Watts 8 Outlets Line Interactive UPS w/ LCD display
Newegg.com - Tripp Lite SMART1500LCD Smart Pro Digital 1500 VA 900 Watts 8 Outlets Line Interactive UPS w/ LCD display (http://www.newegg.com/Product/Product.aspx?Item=N82E16842111052)
$202
Tripp Lite OMNIVS1500 OMNI VS 1500 VA 940 Watts 8 Outlets Line Interactive Tower UPS
Newegg.com - Tripp Lite OMNIVS1500 OMNI VS 1500 VA 940 Watts 8 Outlets Line Interactive Tower UPS (http://www.newegg.com/Product/Product.aspx?Item=N82E16842111050)
$200
CyberPower CP1500PFCLCD UPS 1500VA / 900W PFC compatible Pure sine wave
Newegg.com - CyberPower CP1500PFCLCD UPS 1500VA / 900W PFC compatible Pure sine wave (http://www.newegg.com/Product/Product.aspx?Item=N82E16842102134)
$187
CyberPower Professional PP1500SWT2 1500VA 1000W 7 Outlets UPS
Newegg.com - CyberPower Professional PP1500SWT2 1500VA 1000W 7 Outlets UPS (http://www.newegg.com/Product/Product.aspx?Item=N82E16842102050)
$343
For a UPS which will support more than 1000 watts, I see that Steve Kalle has recommended this unit in some earlier postings:
CyberPower Professional PP2200SW 2200VA 1500W 6 NEMA 5-15R, 2 NEMA 5-20R Outlets UPS
Newegg.com - CyberPower/UPS (http://www.newegg.com/Store/BrandSubCategory.aspx?Brand=1821&SubCategory=72&name=CyberPower-UPS)
Currently sells for $472.
I am aware that this unit requires 20 amp NEMA plugs, but that is not a problem. My studio is already wired with a 12 guage cable fed from a 20 amp breaker. I can easily swap in another 20 amp NEMA outlet, if I were to buy this unit. I suppose that, if I bought this one, I could plug both monitors into it, too.
Anybody else have any experience with this unit?
One thing I do understand is that a VA rating is not the same as the watts actually supplied. Up until now, I just assumed that 1000 VA was "plenty" and blithely went on my way. I now understand a UPS unit rated at 1000VA may actually carry only 500 to 700 watts which would not be enough for the new workstation I'm hurriedly assembling.
So, for a feeding a computer with a 910 watt Power Supply Unit (PSU), what Uninterruptible Power Supply (UPS) specs should I look for?
If my probable maximum load is 800 watts but my PSU is rated higher, should I match the UPS unit to the probable maximum load or to the PSU’s maximum rating? I found these calculator/charts for sizing a PSU, which I am thinking also may be useful for guesstimating the maximum load that a UPS might need to carry:
Power Supplies: How Much Power Do You Need? (http://www.pcpower.com/technology/power_usage/)
Power Supply Selector (http://www.pcpower.com/Power_Supply_Selector.html)
For me, it looks like I might have a maximum load of roughly 775-800 watts. I'm getting a PSU with some headroom. I suspect that ought to match the PSU and UPS, but I do not know.
How does Automatic Voltage Regulation (AVR) work? When running on line voltage (as opposed to batteries), is AVR limited in any way by the power rating for battery operation? Or does AVR basically work like a line conditioner and provide stable power to whatever is hooked up to it regardless of what the UPS unit might supply if it were on battery?
How tightly does AVR have to work to be safe with the newer generations of PSU and CPUs (such as the I7-3930k)? For instance, I have been using a Tripp-Lite G1000UB with the old system. We have dirty power here. Today, the line voltage from the tap was bouncing between 123 volts and 115 volts. (Obviously, I’m in the North America and we’re talking 60 Hz power). I put a VOM on a power-out cable from the Tripp Lite unit. The output from the UPS was hovering around 119.8, although slowly fluctuating as far down as 119.5 and up occasionally to 120.00. Checking specs for UPS units shows a lot of them listing output at “120 v +/- 5%.” That means the tolerance is 6 volts above or below 120 v, right? So, the AVR on my existing unit is working okay, right? The small variation between 119.5 v and 119.9 v is nothing to worry about, right?
Do I need “pure sine wave” output from my UPS if the PSU manufacturer does not spec it in the manual or on the web site? (PC Power & Cooling does not spec it for the 910 Watt unit I have purchased.)
Prices for UPS units rated up to 1000 watts are about half (or less) of the cost of units rated over that. If a power outage occurs while my workstation is, say, in the middle of a long session transcoding 1080 AVCHD to Blu-ray or DVD, I’m guessing that there will not be a full load. A big load, but not the max. The processor will be high but only some of the disks and the raid card will be pulling power. Is this a reasonable assumption or not? Or, with a 900 watt power supply, should I be looking at a UPS unit that carries, say, 1500 watts?
Also, given that price differential, should I plan on using a sub-1000 watt UPS unit exclusively for the workstation and not plug anything else into it? (For example, since I work with twin monitors, should I keep the present Tripp-Lite unit for feeding power to the monitors?)
I’ve assembled a preliminary list of possible candidates for purchase. Depending on what is said in reply to my questions, some of these will drop off the list. But for now, I will be grateful for comments from anybody who has experience with any of these units or who feels knowledgeable enough to help make a selection.
Tripp Lite SMART1500LCD Smart Pro Digital 1500 VA 900 Watts 8 Outlets Line Interactive UPS w/ LCD display
Newegg.com - Tripp Lite SMART1500LCD Smart Pro Digital 1500 VA 900 Watts 8 Outlets Line Interactive UPS w/ LCD display (http://www.newegg.com/Product/Product.aspx?Item=N82E16842111052)
$202
Tripp Lite OMNIVS1500 OMNI VS 1500 VA 940 Watts 8 Outlets Line Interactive Tower UPS
Newegg.com - Tripp Lite OMNIVS1500 OMNI VS 1500 VA 940 Watts 8 Outlets Line Interactive Tower UPS (http://www.newegg.com/Product/Product.aspx?Item=N82E16842111050)
$200
CyberPower CP1500PFCLCD UPS 1500VA / 900W PFC compatible Pure sine wave
Newegg.com - CyberPower CP1500PFCLCD UPS 1500VA / 900W PFC compatible Pure sine wave (http://www.newegg.com/Product/Product.aspx?Item=N82E16842102134)
$187
CyberPower Professional PP1500SWT2 1500VA 1000W 7 Outlets UPS
Newegg.com - CyberPower Professional PP1500SWT2 1500VA 1000W 7 Outlets UPS (http://www.newegg.com/Product/Product.aspx?Item=N82E16842102050)
$343
For a UPS which will support more than 1000 watts, I see that Steve Kalle has recommended this unit in some earlier postings:
CyberPower Professional PP2200SW 2200VA 1500W 6 NEMA 5-15R, 2 NEMA 5-20R Outlets UPS
Newegg.com - CyberPower/UPS (http://www.newegg.com/Store/BrandSubCategory.aspx?Brand=1821&SubCategory=72&name=CyberPower-UPS)
Currently sells for $472.
I am aware that this unit requires 20 amp NEMA plugs, but that is not a problem. My studio is already wired with a 12 guage cable fed from a 20 amp breaker. I can easily swap in another 20 amp NEMA outlet, if I were to buy this unit. I suppose that, if I bought this one, I could plug both monitors into it, too.
Anybody else have any experience with this unit?